06-30-2010, 11:25 AM
I think the discussion started from the seismic point of view (read post#1). Comment:- Post post#1 reads “To avoid catastrophic failure or collapse (brittle collapse), it is required that the hinges (at the plastic stage) form on the
beams, rather than on the columns. For this reason, the codes required the designers to provide a margin of security on the
strength of the column over that of the beam. Having this in mind, is there a situation in which it is justified to provide a
beam of dimension greater than that of the column (say a beam of 500mm x 1200mm which is to be supported on columns
of dimension 500mm x 500mm, assuming that the beam is continuous with the column)? Again, how do we meet-up with
this requirement (I mean, what calculations do we have to carry out as to provide this margin of security between the beam
and the column)?”. This did not at any point refer to seismic analysis nor design, unless if you are saying that structural failure could only be verified if and only if there exists seismic loading.
2. The non-linear analysis offers you the possibility to view the sequence of formation of the plastic hinges. Plastic design is
a different matter. Codes means EC8, our national seismic design code and others. Where have I said that codes forbid
plastic analysis? Don't misinterpret what I have written! If plastic design of structures is the topic of the discussion, please
state it Same source wrote previously “Codes do not require non-linear analysis, so if you design a building using any type of linear analysis you won't be able to
see if hinges appear in columns. Only nonlinear analysis can tell you this. Comment:- is plastic analysis different from non-linear analysis????
3. About the post #2, Where is it said that it is OK to have plastic hinges in columns? The meaning of what it is written in
post #2 is: plastic hinges can form in columns, but in order to have a story mechanism which can lead to collapse, all the
columns in a story must have plastic hinges at the top and at the bottom.
4. The codes allow the following situation: the formation of plastic hinges in the top story columns. The reasons are quite
Obvious. Comment:- Could you please state these obvious reasons?. Remember that what could be an obvious reason to you might not be the same to me.
5. The codes do not require non-linear analysis for current building design. It is rather a designer's choice. Comment:- Please correlate this with yours previously quoted in 2; “…Where have I said that codes forbid plastic analysis?…” Comment continued:-.If the code does not require it, then how can a designer make it a choice to choose from?. Will the designer be operating within or outside the requirements of the code???. Incredible. Please remember that we are discussing engineering but not the legal or court interpretation of terms.
6. The formation of plastic hinges is due to the bending moment. An increased axial force in columns can increase the
bending column capacity (up to a certain limit, of course). But if it is assumed that the columns are designed according to
modern codes (the axial force is limited) than an increased axial force will be better than a decreased axial force. Comment:- Certainly, that is the case and I do not think that we had had any point to disagree on this, except that initially, you were, talking of the column design as if it were a beam design (where moment is the predominant action) .
7. Now returning to plastic hinges I will quote a few things from 'Seismic Design of Reinforced Concrete and Masonry Building':
"The primary aim of the capacity design of columns is to eliminate the likelihood of the simultaneous formation of plastic hinges at both ends of all columns of a story". From same source ”If you do a non-linear dynamic analysis you will see that hinges can appear in columns. If this is the case the overall
stability of the building is not jeopardized. Also, plastic hinges can form in the top story columns (the codes allow the
situation)” Comment:- Note the contradictions between the two statements!!!””..
"Moreover, during the inelastic dynamic response of a frame, when frame distortions similar to those of higher mode shapes
occur, moments may significantly increase at one or the other end of a column, and hence the formation of plastic hinge at
either ends must be expected. Accordingly, relevant codes specify that each end of the such a column be designed and
detailed for adequate rotational ductility." Read again:- “.....that hinges can appear in columns. If this is the case the overall stability of the building is not jeopardized Comment:-”If the stability of the structure is not jeopardized, why should code require that you guide against it by designing and detailing for adequate rotational ductility ?
Same source:-Regardingto to the capacity design of frames against plastic hinging in columns.
"The objective of Eurocode 8 rules for the design of (concrete, steel or composite) moment-resisting frames is to force
plastic hinges out of the columns and into the beams, so that a beam-sway mechanism develops and a soft-story is
prevented". Again …” But, you must take into consideration the fact that the building will not fail if a plastic
hinge forms in a column, rather than in a beam (it is necessary to have plastic hinges in all the columns). Further more the
plastic hinges must form in all the columns both at the top part and at the bottom part”. Comment:- If this statement is true, then why should the objective of Eurocode 8 rules for the design of (concrete, steel or composite) moment-resisting frames be that to force plastic hinges out of the columns and into the beams, so that a beam-sway mechanism develops and a soft-story is prevented. Are there no contradictions?
Also regarding to primary and secondary seismic elements,( from the same source):
"The building structures is taken in design to rely for its earthquake resistance only on its primary seismic elements....The
strength and stiffness of secondary elements against lateral loads is to be neglected in the analysis for the seismic action.
However, their contribution in resisting other actions (mainly gravity loads) should be fully accounted for" Comment:-This issue has nothing to do with either secondary or primary structural members. Comment:- Please read the lead post and interpret accordingly. Again, not all designs concepts adopt the braced frame philosophy. Structures could be design as completely moment resisting, as such this assertion has nothing to do with this discuss.
There is also a section about "Special Requirements for the design of secondary seismic elements" which describes the
design of these elements in the same above-mentioned source. Comment:- Like I sounded several times before now, seismic design is a different issue from the case at hand. Please interpret original post in its original context. I hope that we are done with this. How differently we could understand same simple issue.!!!
Now I have a pavilion with two end access staircases leading unto a central platform. The end staircases are each of span 6.5m on plan, rising from the ground level onto the platform at 3m above the ground level. The platform itself is of span 30m. So how do we proportion this pavilion? (see the uploaded image above for further details )
Regards
Teddy