OPTIMIZED USE OF THE OUTRIGGER SYSTEM TO STIFFEN THE COUPLED SHEAR WALLS IN TALL BUILDINGS
Author: NAVAB ASSADI ZEIDABADI , KAMAL MIRTALAE AND BARZIN MOBASHER | Size: 250 KB | Format: PDF | Quality: Unspecified | Publisher: NAVAB ASSADI ZEIDABADI , KAMAL MIRTALAE1 AND BARZIN MOBASHER | Year: 2004 | pages: 19
Based on the conventional yet accurate continuum approach, a general analysis is presented for a pair of coupled
shear walls, stiffened by an outrigger and a heavy beam in an arbitrary position on the height. Subsequently, a
parametric study is presented to investigate the behavior of the structure. The optimum location of the outrigger
and the parameters affecting its position were also investigated. The results showed that the behavior of the structure
can be significantly influenced by the location of the outrigger. It was also indicated that in most ordinary
cases the best location of the structure to minimize top drift is somewhere between 0·4 to 0·6 of the height of the
structure. Though this method is not a substitute for the finite element method, it gives an initial simple solution
to determine the size and position of outrigger, stiffening beam and coupled shear walls in the preliminary design
stages.