Civil Engineering Association eBooks Codes, Manual & Handbook AISC AISC 341: Seismic Provisions for Structural Steel Buildings
Threads: 1,298
03-07-2011, 06:27 AM (This post was last modified: 01-12-2022, 11:23 AM by Administrator.)
ANSI/AISC 341-05 Seismic Provisions for Structural Steel Buildings Including Supplement No. 1
Size: 5.12 MB | Format: PDF | Publisher: ANSI/AISC | Year: 2005 | pages: 334
[Image: 74999779993016367341.jpg]
The Seismic Provisions for Structural Steel Buildings, hereinafter referred to as these Provisions, shall govern the design, fabrication and erection of structural steel members and connections in the seismic load resisting systems (SLRS) and splices in columns that are not part of the SLRS, in buildings and other structures, where other structures are defined as those structures designed, fabricated and erected in a manner similar to buildings, with building-like vertical and lateral load-resisting-elements. These Provisions shall apply when the seismic response modification coefficient, R, (as specified in the applicable building code) is taken greater than 3, regardless of the seismic design category. When the seismic response modification coefficient, R, is taken as 3 or less, the structure is not required to satisfy these Provisions, unless specifically required by the applicable building code. These Provisions shall be applied in conjunc tion with the AISC Specification for Structural Steel Buildings, hereinafter referred to as the Specification. Members and connections of the SLRS shall satisfy the requirements of the applicable building code, the Specification, and these Provisions. Wherever these provisions refer to the applicable building code and there is no local building code, the loads, load combinations, system limitations and general design requirements shall be those in SEI/ASCE 7.
User Note: The applicable building code generally restricts buildings designed with an R factor of 3 or less to seismic design categories (SDC) A, B or C; however, some systems such as cantilever columns that have R factors less than 3 are permitted in SDC D and above and these Provisions apply. See the applicable building code for specific system limitations. Part I includes a Glossary that is specifically applicable to this Part, and Appendices P, Q, R, S, T, W and X.
[-] The following 26 users Like ir_71's post:26 users Like ir_71's post
  • cace-01, kowheng, Grunf, malc, zainseiya, zrilek, jcbv, mrgoodboydatdat, Dell_Brett, vinnunsam, toa011, seriousboy, nuttapolk, robertsas, ting tsai huang, pezhmankhan, Clouseau, fer962933, pedzaquino, ISTRAKTURA, miquan, joradu, Svetoslav, Jackass, TAFATNEB, oanm2000
 Diquan
Costa Rica
User ID: 41
Threads: 27
Likes: 1,205 in 128 posts
Given Likes: 781
02-29-2012, 04:56 PM
Seismic Provisions for Structural Steel Buildings (ANSI/AISC 341-10), Second Printing + Revision and Errata List (January 10, 2012)
Author: AISC | Size: 13 MB | Format: PDF | Quality: Unspecified | Publisher: AISC | Year: January 2012
This ANSI-approved specification is a companion to the Specification for Structural Steel Buildings (ANSI/AISC 360-10) that extends coverage to the connection detailing and member design requirements for structural steel and composite systems in high-seismic applications. The 2010 edition of the AISC Seismic Provisions and Commentary supersedes and is an update of the 2005 edition. A number of major changes were made in this edition, and a cross reference list following the table of contents provides a reference to the corresponding section of the 2005 Seismic Provisions. Both LRFD and ASD methods of design are incorporated. Dual-units format provides for both U.S. customary and S.I. units.
[-] The following 10 users Like Diquan's post:10 users Like Diquan's post
  • pedzaquino, kowheng, simanta, Dell_Brett, PSMUSACALA, malc, jcbv, carolinandra, arceon, bigone
 mybest
Indonesia
User ID: 32155
Threads: 283
Likes: 3,957 in 566 posts
Given Likes: 686
02-29-2012, 05:23 PM
This is free publication from AISC
Follow this link
Find out more here
[-] The following 8 users Like mybest's post:8 users Like mybest's post
  • Jackass, kowheng, Dell_Brett, seriousboy, bigone, loyal85, Mohammad6299, pram
 88FeNIX
User ID: 24521
Threads: 39
Likes: 229 in 52 posts
Given Likes: 303
11-01-2012, 01:15 PM
Dear All,,
The above links are dead. Please upload.
Thanks in advance.
[-] The following 1 user Likes 88FeNIX's post:1 user Likes 88FeNIX's post
  • ans575
 lisine
Vanuatu
User ID: 17927
Threads: 272
Likes: 11,712 in 1,306 posts
Given Likes: 4630
11-01-2012, 01:24 PM
[-] The following 6 users Like lisine's post:6 users Like lisine's post
  • blaze, oanm2000, 88FeNIX, lednar_ved, slowet, k2kyaw
 asrhael
Chile
User ID: 23449
Threads: 6
Likes: 179 in 21 posts
Given Likes: 26
04-22-2014, 12:24 PM
AISC Seismic Provisions 1997 + Supplements (Nº1-1999 & Nº2-2000)
Author: American Institute of Steel Construction, INC (AISC) | Size: 1.5 MB | Format: PDF | Quality: Unspecified | Publisher: American Institute of Steel Construction, INC (AISC) | Year: 1997, 1999, 2000 | pages: 160+12+35
This AISC Seismic Provisions for Structural Steel Buildings is a separate document that addresses one such topic: the design and construction of structural steel and composite structural steel/reinforced concrete building systems in seismic regions.
[Image: comments.png]
Direct download from Dropbox.
[-] The following 6 users Like asrhael's post:6 users Like asrhael's post
  • Rapaig, cace-01, Mohammad6299, ruaumoko, milova, ting tsai huang
 Mohammad6299
User ID: 42302
Threads: 261
Likes: 7,913 in 854 posts
Given Likes: 4212
04-22-2014, 02:30 PM
ANSI/AISC 341-02: Seismic Provisions for Structural Steel Buildings, including Supplements No. 1 and 2
Size: 1.2 MB | Format: PDF | Quality: Original preprint | Publisher: American Institute of Steel Construction (AISC) | Year: 2002 | Pages: 214
[Image: 57959821045005704275.jpg]
The AISC Seismic Provisions for Structural Steel Buildings, dated 2002, is a full revision of the 1997 version of this document, including Supplements Number 1 (dated February 15, 1999) and 2 (dated November 10, 2000).
This American National Standard, developed by the AISC Task Committee 9 on Seismic Design and approved by the AISC Committee on Specifications, is the most current specification in the United States addressing the design and construction of structural steel and composite structural steel/reinforced concrete building systems for seismic demands. In addition to the inclusion of the recent Supplements No. 1 and 2, revisions resulting from new information generated by the FEMA/SAC project and other sources are incorporated. One major change is related to the referencing of ASCE 7-02, Minimum Design Loads for Buildings and Other Structures, which allows the 2002 Seismic Provisions to be incorporated by reference into both the 2002 NFPA 5000 and the 2003 International Building Code. Both codes use ASCE 7-02 as their basis for design loading. Additional specific changes included in the 2002 Seismic Provisions include the following:
- A clarification to the glossary to verify that chord and collector/drag elements in floor diaphragms are considered to be part of the Seismic Load Resisting System.
- Additional requirements for the toughness of filler metals to be used in complete-joint-penetration groove welds in Intermediate and Special Moment Frame systems.
- A revision to clarify member slenderness ratio requirements and better coordinate with the LRFD provisions.
- Increasing the Moment Frame column splice requirements to reflect the FEMA/SAC recommendations.
- Requiring that splices of columns that are not part of the Moment Frames develop a minimum shear force.
- Clarifying Column Base design demands for various systems.
- Adding a section on the use of H-pile members.
- Clarifying lateral bracing requirements of Moment Frame beams, including the provision of a required stiffness to be consistent with Section 3 of LRFD.
- Increasing SMF web Connection design requirements to be consistent with the FEMA/SAC recommendations.
- Adding a new appendix (Appendix P) that defines procedures to be used in the pre-qualification of moment Connections.
- Incorporating FEMA/SAC recommendations for weld access holes in OMF systems.
- Incorporating FEMA/SAC recommendations for the removal of weld backing and run-off tabs in OMF systems, including grinding surfaces to adequate smoothness.
[-] The following 7 users Like Mohammad6299's post:7 users Like Mohammad6299's post
  • blaze, PinkPant, asrhael, malc, ting tsai huang, Dell_Brett, harsono
Likes: 12,075 in 1,233 posts
03-01-2017, 02:53 PM
ANSI/AISC 341-16, Seismic Provisions for Structural Steel Buildings
Size: 13.3 MB | Format: PDF | Quality: Original preprint | Publisher: AISC | Year: 2016 | pages: 476
[Image: 80976120634067309586.jpg]
The Seismic Provisions are a companion to the Specification for Structural Steel Buildings that extends coverage to the connection detailing and member design requirements for structural steel and composite systems in high-seismic applications. The 2016 edition of the AISC Seismic Provisions and Commentary supersedes and is an update of the 2010 edition. Both LRFD and ASD methods of design are incorporated. Dual-units format provides for both U.S. customary and S.I. units.
[-] The following 29 users Like pezhmankhan's post:29 users Like pezhmankhan's post
  • amindoxiti, ASEC, hatkam, blaze, oanm2000, faros3000, malc, Dell_Brett, uncblue, gulilero, subin91, zrilek, ssobhan, slowet, cheosmith, promo8, monter, avge, Aviator, Veggeta, blackjack, pedzaquino, pram, febo927, davegabj, jonygut, spat, milova, kowheng
 sabooryan
Senior Member
User ID: 163767
Threads: 77
Likes: 1,962 in 167 posts
Given Likes: 547
05-21-2018, 08:43 PM
please re-upload AISC seismic provisions 1997, many thanks
[-] The following 1 user Likes sabooryan's post:1 user Likes sabooryan's post
  • hatkam
Threads: 750
Likes: 8,270 in 1,355 posts
Given Likes: 88
#10
01-12-2022, 10:58 AM
AISC 341-22 (Public Review Draft): Seismic Provisions 7 for Structural Steel Buildings
| Size: 1.88 MB| Format: PDF| Quality: Original preprint| Publisher: AISC| Year: 2022| pages: 164
[Image: 76736051742060535444.png]
  • Administrator , babakfeyzi, cheosmith, milova, kowheng, simanta, PinkPant, cace-01, highcivil
Pages (2): 1 2 Next »
  AISC - Steel Design Guides Administrator 75 84,986 06-13-2026, 09:38 AM
  AISC 327: Seismic Design Manual weichunc 16 14,502 06-13-2026, 09:27 AM
  AISC - Steel Construction Manual dinu69in 26 26,704 06-10-2026, 12:17 PM
  ANSI/AISC N690: Specification for Safety-Related Steel Structures for Nuclear Facil ir_71 5 12,843 08-18-2025, 07:07 AM
  AISC Model Review and Approval for Structural Steel poolmand 0 3,585 04-29-2024, 07:29 AM
  AISC BIM & VDC FOR STRUCTURAL STEEL poolmand 0 3,169 04-29-2024, 07:27 AM
  AISC Conference: Composite Construction in Steel and Concrete VIII poolmand 0 2,978 12-04-2023, 09:17 AM
