Seismic performance of a 12-storey ductile concrete shear wall system designed according to the 2005 National building code of Canada and the 2004 Canadian Standard Association standard A23.
Author: Yannick Boivin and Patrick Paultre | Size: 1.1 MB | Format: PDF | Quality: Unspecified | Publisher: Can. J. Civ. Eng. 37: 1β16 (2010) doi:10.1139/L09-115 | Year: 2010 | pages: 16
![[Image: 25503254115967420132.png]](https://pic.civilea.com/images/25503254115967420132.png)
This paper presents an assessment of the seismic performance of a ductile concrete core wall used as a seismic
force resisting system for a 12-storey concrete office building in Montre Β΄al, designed according to the 2005 National building
code of Canada (NBCC) and the 2004 Canadian Standards Association standard A23.3. The core wall consists of a
cantilever wall system in one direction and a coupled wall system in the orthogonal direction. The building is analyzed in
the nonlinear regime. The main conclusion from this work is that the capacity design shear envelope for the studied wall
structure largely underestimates that predicted, primarily in the cantilever wall direction, and this in turn significantly increases
the risk of shear failure. This issue is essentially due to (i) an underestimation by the new NBCC spectral response
acceleration of the higher mode responses of a reinforced concrete wall structure whose seismic response is dominated by
higher modes; and (ii) a deficiency in the capacity design method in estimating the wall shear demand on such walls, even
when their behavior is lightly inelastic.