Normalized Axial force by EC8
Hi
My question have to concern with normalized axial force by EC into columns
Under thew desired ductility conditions EC require this conditions
ni=Ned/(Ac*fcd) <= 0.55 for DCH ... 1
ni=Ned/(Ac*fcd) <= 0.65 for DCM ... 2
ni=Ned/(Ac*fcd) <= 0.75 for DCL .... 3
Where Ned is axial force ( kN for ex.) given from seismical situations.
My question is
Which value of Axial force must be included in equations 1,2, and 3
N = Ng+0.3NP+Ns or N = 1.35Ng+1.5Np
Or equations 1,2,3 must be checked with both values of axial forces
Any reference or any example would be helpfull,
z.g.
United States of Albania
[-] The following 1 user says Thank You to giga for this post:
  • DamirDz
Quote:N = Ng+0.3NP+Ns
this value
[-] The following 3 users say Thank You to rigid_joint for this post:
  • theanhpe, giga, DamirDz
dear Rigid_Joint
Thanks for reply
any reference or any example if you have would bee very helpfull.
I agree to you that the axial force should be taken from seismic design situations
(Ng+0.3Np+Ns), but i have seen in some books that is taken 1.35Ng+1.5Np, and this have confused mee very much.
One reference book in which the author use N = 1.35Ng+1.5Np and Ng+0.3Np+Ns, is book of author Jure Radiq - Betonske Konstrukcije - ( is in croatian Language).
z.g.
the one and only right combination is the Ng+0.3q+Nseismic.
because is related with seismic design situation
which value of Gamac should be used for calculating of fcd.
Dear giga, i would advise you not to take to much reference from the Jure Radic book, one example being this you mentioned here. I had the same doubt a while ago just because of that book.
One other reference i can come up with now is the El Ghazouli (don't know the exact spelling) book on EC8 which you can find here on the forum.
Best regards!
DamirDz
[-] The following 1 user says Thank You to DamirDz for this post:
  • giga
Quote:which value of Gamac should be used for calculating of fcd.
γc=1.5