10-14-2010, 05:09 AM
RedHorse wrote:-
....minimum slab thickness, cantilever = L/10
thus; h = 1750/10 = 175mm (min.), but needs to check deflection....
Comment:-
I think that you are using a code other than BS or the EUROCODE. For BS or EUROCODE, span/effective depth ratio =7 (not 10). Well, that is a code issue as such we may not have to deliberate on that.
RedHorse wrote:-
…sample loading from a 4 storey bldg i designed (uniformly distributed load only)
SECOND/FOURTH FLOOR SLAB:
DL: RC SLAB = 0.115m(24kN/m.m.m) = 2.76kN/m/m
…
Comment:
Could you please indicate the span of the cantilever slab that you are using a thickness of 115mm to design? I believe that that should be a very short cantilever indeed as such will have nothing to do with the issue in discuss.
Regards
Teddy