Design of 5,000 Gal. Elevated Tank using Staad Pro.
![[Image: 90912990629038007516.jpg]](https://pic.civilea.com/images/90912990629038007516.jpg)
![[Image: screen.png]](http://forum.civilea.com/postgen/screen.png)
![[Image: 20341599838255508318.jpg]](https://pic.civilea.com/images/20341599838255508318.jpg)
![[Image: Download.png]](http://forum.civilea.com/postgen/Download.png)
Code:
Content of this section is hidden, You must be registered and upgrade your account to see this content.See this link to read how you can remove this limitation:
๐ CLICK HERE ๐
|
Design of 5,000 Gal. Elevated Tank using Staad Pro.
![]() ![]() ![]() ![]() Code: Content of this section is hidden, You must be registered and upgrade your account to see this content.See this link to read how you can remove this limitation: ๐ CLICK HERE ๐
The following 29 users Like ranger's post:โข kowheng, lirizen, Dell_Brett, sasan7351, Quantumm,
05-19-2012, 09:56 AM
A new link
Code: Content of this section is hidden, You must be registered and upgrade your account to see this content.See this link to read how you can remove this limitation: ๐ CLICK HERE ๐
The following 17 users Like scorpion07's post:โข pezhmankhan, slowet,
12-17-2012, 12:50 PM
i am just a bit worried about posting a file which have not been verified if it is properly done or not, upon initial review of the file I find it that there are a lot of parameters that have been neglected and it is also not in compliance with the code. the internal pressure of the fluid has been neglected this will induce impulsive and convective pressure on the side wall during earthquake on top of the static pressure. another very important issue is the weight of the fluid itself is ignored but the live load value is included in the weight definition for seismic mass this is absolutely wrong.
furthermore, the force reduction factor for building cannot be used for this type of structure. Probably what I would have done if I am the author of the file is to issue a disclaimer that anyone who would like to use the file should verify the same. Without the disclaimer this would be very dangerous for those who will just blindly adopt it as a reference. just my two cents.
The following 14 users Like ASEC's post:โข LiviuM, pelon2040, aslam, lednar_ved, 3fan, p_vosoughi, Andrew seah,
12-18-2012, 02:00 AM
@asec
Your point is well taken. Even the "Building Codes" and well established "Commercial Softwares" have disclaimer about the responsibility of the User for the implementation. Engineers or Architects who are using these codes ultimately responsible for the final design. Codes are minimum guidelines and requirements. Quote:Building Code Requirements for Structural Concrete (ACI 318-11)and Commentary Carefully reading above would clearly explain this. Best regards |
| Possibly Related Threads… | |||||
| Thread | Author | Replies | Views | Last Post | |
| Oil Storage Tank Design Calculation as per API 650 | duazo2009 | 5 | 19,841 |
02-09-2019, 08:02 AM Last Post: kowheng |
|
| Design of 5,000 Gal. Elevated Tank ( conical bottom ) using Staad Pro. | ranger | 1 | 10,429 |
03-12-2011, 01:29 AM Last Post: ASEC |
|